My son's 2000 Chevy Silverado's air compressor will not kick on.We have put a gauge on it from a refill can of refridgerant and it says it was in the green zone. We have replace both low and high pressure ports. When we replaced the low the compressor kicked on and worked for a day or 2 and then stopped again. We replaced the High pressure side and no change. The compressor kicks on and cools when you jump the AC relay out with a piece of wire. We are curious as to what other issues we could have that would stop it from engaging with what we've already done. Could it be voltage issue with pressure switches wiring plug and if so should it be at 12vdc? Any other info would be greatly appreciated by myself and my son since it's his truck. Mid to high 90's already in central Illinois. 🥵🥵🥵
Last edited by GraniteRam16; June 17th, 2024 at 9:05 PM.
#3
CF Senior Member
![Default](/forum/images/icons/icon1.gif)
First off, get a real set of HVAC gauges so you can monitor both the high pressure and low pressure sides of the HVAC system at the same time. The gauges on those cans of refrigerant are notoriously inaccurate.
If there is not enough refrigerant in the system, the compressor will not engage because the low pressure switch will not close. If there is too much refrigerant in the system, the compressor may not engage because the high pressure switch has opened.
You may have a leak in the system someplace. You mentioned that you replaced the low and high pressure ports. Those might not be tight enough or the new ones could be defective.
These systems are filled by weight of refrigerant and not by pressure. The only way to accurately recharge them is to recover the refrigerant present in the system, evacuate the system using a vacuum pump for 30 to 60 plus minutes and then see if it holds vacuum for at least 15 minutes, and then add the appropriate amount of refrigerant by weight.
Good Luck!
If there is not enough refrigerant in the system, the compressor will not engage because the low pressure switch will not close. If there is too much refrigerant in the system, the compressor may not engage because the high pressure switch has opened.
You may have a leak in the system someplace. You mentioned that you replaced the low and high pressure ports. Those might not be tight enough or the new ones could be defective.
These systems are filled by weight of refrigerant and not by pressure. The only way to accurately recharge them is to recover the refrigerant present in the system, evacuate the system using a vacuum pump for 30 to 60 plus minutes and then see if it holds vacuum for at least 15 minutes, and then add the appropriate amount of refrigerant by weight.
Good Luck!